 Post subject: Boiler External Piping
PostPosted: Thu Mar 11, 2010 3:07 pm 
Offline
----------------
----------------

Joined: Tue Dec 01, 2009 1:55 pm
Posts: 270
Location: DESCON Engineering Limited, Pakistan
As per ASME Section I, addenda 2009.

When the drain piping shall be considered as blow-off piping?

what is the surface blowoff piping ?

I am very confused between bllowdown, drain, continous blow down, surface blowoff, blowoff piping while reading out PG-58, PG-59.

Best Regards,

Nasir

_________________
Thanks & Regards,
Nasir
Welding Engineer
DESCON Engineering Limited.
Lahore, Pakistan.
Mobile # 0092-336-4145402


Top
 Profile  
 
PostPosted: Sat Mar 13, 2010 12:06 am 
Offline
----------------
----------------
User avatar

Joined: Sat Dec 15, 2001 1:00 am
Posts: 656
Javed Nasir wrote:
As per ASME Section I, addenda 2009.

When the drain piping shall be considered as blow-off piping?

what is the surface blowoff piping ?

I am very confused between bllowdown, drain, continous blow down, surface blowoff, blowoff piping while reading out PG-58, PG-59.

Best Regards,

Nasir


Iaved, me either don't remember the meaning of blow-down vs blow-off but I know the functions.

The boiler receives distilled water where a very small amount of salts remains. And steam with no salts contained. With the time the water which remains in the boiler becomes richer in salts. That's why a surface blow-off piping removes water to renew it and keep salt concentration low. This system called also de-concentration of salt from the water (literally translated from Italian), is continuous.

A blow down pipe is required at the bottom of the boiler to remove, when the boiler is in pressure, the deposited mud. Mud is formed because the additives remove the salts and aggregate them in mud. It is intermittent.

A drain is required in the lowes part of the boiler to discharge all water when the boiler is emptied to be out of service or repaired.

The drain can be operated also as a blow-down, in which case it shall have double valve

Mauro


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 2 posts ] 

All times are UTC + 2 hours


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
cron
Powered by phpBB® Forum Software © phpBB Group

phpBB SEO