Hi,
The difference between fired and unfired vessels is the fire!
Different definitions are established in the laws and Codes of this world. In the actual case I recommend to look into the applicable boiler law at the location of installation:
1- If a vesses is exposed to heat from the combustion of fuel it is fired
2- If a vesses is exposed to radiation from the combustion of fuel it is fired
3- If a vesses is exposed to heat from a fire, or electric heating it is fired
Case 1 and 2 exclude process heat, case 3 includes!
If the vessel is fired, as per Preamble of Section I, it may be built to Section I or VIII.
If built to Section VIII, Div. 1, UW-2 addresses special requirements, and the nameplate shall be stamped "DF" under the U-stamp. The MDR will specify Direct firing as well.
Does this help?
|