Appendix S , API 650
S 4.10 Hydrostatic testing
S.4.10.2 The materials used in the construction of stainless steel tanks may be subject to severe pitting, cracking, or rusting if they are exposed to contaminated test water for extended periods of time. The Purchaser shall specify a minimum quality of test water that conforms to the following requirements:
a. Unless otherwise specified by the Purchaser, water used for hydrostatic testing of tanks shall be potable and treated, containing at least 0.2 parts per million free chlorine.
b. Water shall be substantially clean and clear.
c. Water shall have no objectionable odor (that is, no hydrogen sulfide).
d. Water pH shall be between 6 and 8.3.
e. Water temperature shall be below 50°C (120°F).
f. The chloride content of the water shall be below 50 parts per million, unless specified other wise by the Purchaser.
S.4.10.3 When testing with potable water, the exposure time shall not exceed 21 days, unless specified otherwise by the Purchaser.
S.4.10.4 When testing with other fresh waters, the exposure time shall not exceed 7 days.
S.4.10.5 Upon completion of the hydrostatic test, water shall be completely drained. Wetted surfaces shall be washed with potable water when nonpotable water is used for the test and completely dried. Particular attention shall be given to low spots, crevices, and similar areas. Hot air drying is not permitted.