UG-100 Said:
Quote:
The visual inspection of the vessel at the required test
pressure divided by 1.1 may be waived provided:
(1) a suitable gas leak test is applied;
(2) substitution of the gas leak test is by agreement
reached between Manufacturer and Inspector;
(3) all welded seams which will be hidden by assembly
be given a visual examination for workmanship prior
to assembly;
(4) the vessel will not contain a “lethal” substance.
Does this paragraph mean that, the AI can give up witness the inspection if above 1~4 meet/
is there any guide for the gas leak test adopted by ASME VIII-1.--Does the ASME V Artical 10 appenix 1 would be chosen,
if so, how to chose the bubble solution, code said
Quote:
Household soap or detergents are
not permitted as substitutes for bubble testing solutions.