Dear Gentlemen, i encountered a question, at one site, no adequate fresh water for hydro test, so now the contractor planning to take lake water as substitution, i think the water quality should be testfied, but as water quality requirement, i only know the Chloride ion should be less than 25 ppm, so is there any other requirement for the testing water, pls advise, thanks.
by the way, the equipment is LPG spherical tank.


Top
 Profile  
 
PostPosted: Sun Feb 27, 2011 2:18 pm 
Offline
----------------
----------------
User avatar

Joined: Sat Dec 15, 2001 1:00 am
Posts: 657
fred.wang wrote:
Dear Gentlemen, i encountered a question, at one site, no adequate fresh water for hydro test, so now the contractor planning to take lake water as substitution, i think the water quality should be testfied, but as water quality requirement, i only know the Chloride ion should be less than 25 ppm, so is there any other requirement for the testing water, pls advise, thanks.
by the way, the equipment is LPG spherical tank.


Nothing in the Code
mauro


Top
 Profile  
 
PostPosted: Wed Apr 13, 2011 8:06 pm 
Offline
----------------
----------------
User avatar

Joined: Mon Jan 22, 2007 11:01 am
Posts: 14
Location: Farwaniya,Kuwait
For the Carbon Steel Vessels Chloride is not mandatory the Potable water is acceptable,however for Stainless Steel Vessels Chloride content is specified by most of the clients to be 25ppm.

_________________
Thanks & Best Regards!
K.Shabu Mathew

"A successful man is one who can lay a firm foundation with the bricks others have thrown at him". By David Brinkley


Top
 Profile  
 
PostPosted: Sat Apr 16, 2011 1:53 pm 
Offline
----------------
----------------
User avatar

Joined: Sat Dec 15, 2001 1:00 am
Posts: 657
Shabu Mathew wrote:
For the Carbon Steel Vessels Chloride is not mandatory the Potable water is acceptable,however for Stainless Steel Vessels Chloride content is specified by most of the clients to be 25ppm.


25ppm is also the maximum content of chloride permitted in potable water (in Europe).
Mauro


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 4 posts ] 

All times are UTC + 2 hours


Who is online

Users browsing this forum: No registered users and 0 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
Powered by phpBB® Forum Software © phpBB Group

phpBB SEO